I have a question about generator wiring practice on boats. I have recently encountered three instances of boats with generators tripping ground fault breakers recently installed on many docks.

In all three it was found the ground wire  (green) was connected to shore power neutral at the generator. In all three cases disconnecting this  fixed the ground fault trips.

From articles I have read it never permissible to connect ground to neutral on a boat, though it is required by code in residential electric.

So my question is why did boat manufacturers connect ground to neutral on generator installations and is it ok to remove the connection?

If I remove  the connection do I need to provide a way to reconnect when on generator power and disconnect on shore power?

Thanks

John Brock

Views: 76

Reply to This

Replies to This Discussion

In order for the breakers to trip, the neutral has to be grounded. Otherwise there is no path back to the source (in this case the generator) to complete the circuit so the breakers can trip. If the neutral is not grounded, then if there is a fault to ground nothing would happen and then a dangerous condition would exist if there was an accidental connection to ground, maybe through a person - hence shock hazard.

The tripping of the shore power GFI should be prevented by the selector switching between shore power to generator power by disconnecting the generator neutral when in shore power mode, and when in generator mode, the shore power neutral would be disconnected. This is how my panel works as I have two mains that have an interlock so only one is on at a time. The main breakers are two pole disconnecting both hot and neutral at the same time. If you had a transfer switch it must also transfer the neutral. The moral of the story is that the shore power neutral and the generator neutral cannot be landed together and must switch just like the hot wires. This would apply to a 120/240V system as well.

The transfer switch looks like it breaks both line and neutral. Must be the genny neutral is connected somewhere else to shore power neutral.

John

Thinking about this the generator does have a line and neutral. All the circuits are powered by this pair of wires. So the breaker would have a path to trip without a green ground wire involved. This is for an  internal failure of a device or a short circuit or any fault where too much current is drawn

If a fault to ground occurred then no path to trip. Results in a hazardous situation

Is that the correct view of it?

John

Yes I think you’ve got it. A short circuit between hot and neutral would cause an immediate over current condition and should result in an immediate breaker trip. The same for any over current condition it just might take longer for the breaker to respond depending on the magnitude of the over current. The purpose for the green grounding conductor is to bond the exterior frames of equipment and appliances back to the source to establish a sure return path with a low resistance. The neutral is then intentionally connected to the ground in this case the generator frame where the green grounding conductor are also connected. This way if there is an unintentional connection between the hot and the frame of any equipment then we have a path to trip the breakers. In an ungrounded system the first fault doesn’t do anything so it would not be detected and could effectively energize the frames of equipment or appliances. Then someone touches the appliance and something that is grounded and gets shocked by completing the circuit.

A GFI works by sensing a balance between the hot and neutral. If there is any unbalance then it will trip. Anytime the neutral and ground get connected together downstream of the GFI it will cause an unbalance as some power will return through the ground.

You’ll need to check your neutrals from both the generator and shore power to make sure they are not connected together. When on shore power only that neutral should be connected through to the neutral bus bars in the breaker panel. When in generator mode the shore neutral should be disconnected and only the generator neutral connected to the neutral bus in the panel. That should resolve the issue. The green grounds should always be connected and can be all together.

Hope that helps!

Reply to Discussion

RSS

Club News

WANTED: National Chris-Craft Commander Club Rendezvous Hosts!!

A National Rendezvous is a gathering of club members and their beloved Commanders. It is a great place to see some beautiful boats, make new friends and catch-up with old friends. It is always interesting to see what is different on the same model boat and a great place to get ideas, tips & tricks.

If you would like to host a rendezvous, the Executive Committee will assist you with ideas, registration, and anything else you might need.  

If your marina, or a marina near you, could house additional boats for a weekend and if you have several Commanders in your area, we encourage you to consider hosting a rendezvous.

Please contact Char Pike, at rendezvous.commanderclub@gmail.com, with your questions.

To see information on past rendezvous, Click Here

_________________________

Help Wanted!!!

New Faces, New Perspectives - Executive Committee Openings to start in January 2020

Would you like to be more active in the Commander Club? Would you like to help chart our course? Are you willing to commit the time, energy and creativity needed to assist us in promoting and supporting our mission?

We are searching for new faces and new perspectives. Positions start in January 2020 for a two year term.

There are four positions available. Chief Commander, Treasurer, Public Relations Chair and Membership Chair.

Duties for each position are located in the bylaws https://commanderclub.com/page/bylaws

More details about each position here.

The Executive Committee (EC) convenes monthly via conference call. Meetings typically last 90 minutes or less. Most work done via e-mail. Each job has its own time commitment depending on club activities. Current EC members will mentor you.

Interested in any of these positions?

Please drop Char Pike an e-mail at archivist.commanderclub@gmail.com

________________

SuperDisc 14.0 and Resource Collection 4.0 Available Now!

SuperDisc 14.0 is an electronic encyclopedia of every aspect of Commander maintenance and repairs. The information on the disk is retrieved from the discussion forum and e-mail list, but organized in a way that makes information easy to find and use. SuperDisc is available on USB flash drive

Click here for more details https://commanderclub.com/page/superdisk

The SuperDisc 14.0 Complete Edition is for first time buyers of SuperDiscs.

The SuperDisc 14.0 Upgrade Edition is intended for those who wish to upgrade their SuperDisc 1.0 through 13.0. Each year we add over 1,000 posts. Don’t miss out.

Resource Collection 4.0 is great to own too!!!

The Resource Collection 4.0 contents include CC Catalogs and Brochures. CC Service Bulletins, CC Price Lists. Engine & Transmission Manuals. Dick Avery sketches and drawings, a folder for every Commander model, and all kinds of technical and interesting stuff. Over 187 folders and 2,563 Files. A true “Treasure Trove” for the Commander owner!

We thank you for supporting the club with your purchase of SuperDisc14.0 and/or Resource Collection 4.0. We hope you find it to be the value we feel it is, and trust you will enjoy the other benefits your payment will help provide. It’s your payment that helps to support the activities of this dues free organization that has grown from 12 members in 1999 to well over 4000 members in 2019.

To order now click here!

     

© 2019   Created by CCCC Webmaster.   Powered by

Badges  |  Report an Issue  |  Terms of Service